Feeder Bus Duct Voltage Drop

Status
Not open for further replies.

dmarchand73

New member
I am looking for a formula to calculate the voltage drop of a 1600Amp feeder bus duct from the main switchboard to meter stacks. I have a total distance of 150 feet of bus duct.
 
Re: Feeder Bus Duct Voltage Drop

How about....

single phase: Voltage drop = K x L x 2 x I / CM

3 phase: Voltage drop = K x L x 1.732 x I / CM

K = 12.9 for CU and 21.2 for AL
L = length of run
I = amps
CM= cir mils (found in NEC table 8)
 