D dmarchand73 New member Dec 13, 2005 #1 I am looking for a formula to calculate the voltage drop of a 1600Amp feeder bus duct from the main switchboard to meter stacks. I have a total distance of 150 feet of bus duct.
I am looking for a formula to calculate the voltage drop of a 1600Amp feeder bus duct from the main switchboard to meter stacks. I have a total distance of 150 feet of bus duct.
bob Senior Member Location Alabama Dec 13, 2005 #2 Re: Feeder Bus Duct Voltage Drop Check here http://www.cda.org.uk/megab2/elecapps/pub22/index.htm http://www.copper.org/applications/busbar/ampacity/busT4.htm http://64.90.169.191/resources/pub_list/power-quality.html [ December 13, 2005, 11:36 AM: Message edited by: bob ]
Re: Feeder Bus Duct Voltage Drop Check here http://www.cda.org.uk/megab2/elecapps/pub22/index.htm http://www.copper.org/applications/busbar/ampacity/busT4.htm http://64.90.169.191/resources/pub_list/power-quality.html [ December 13, 2005, 11:36 AM: Message edited by: bob ]
G gregsparky1 Member Dec 14, 2005 #3 Re: Feeder Bus Duct Voltage Drop How about.... single phase: Voltage drop = K x L x 2 x I / CM 3 phase: Voltage drop = K x L x 1.732 x I / CM K = 12.9 for CU and 21.2 for AL L = length of run I = amps CM= cir mils (found in NEC table 8)