W have 4 motors each motor has its own control Panel, 3 phase, 400 V and its rating as follow:
1- Press: 2 Nos. each 250 HP
2- Vertical Dryer: 1 No. , 125 HP
3- Glazing : 1 No. , 75 HP
I did calculations to obtain the conductor & C.B for each motor as follow:
1- Press: I full load = 353 A , so the conductor must have 1.25*353= 441 A
cable length = 155 m then the correct size after applying all factors is 2(3C x 150 mm2 CU/XLPE/PVC) ;{300 MCM} with voltage drop = 2.12 %
C.B rating : 630 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 353 x 2.5 =882 A, lead to 800 A)
2- Vertical dryer: I full load= 177 A , so the conductor must have 1.25*177= 221 A
cable length = 150 m then the correct size after applying all factors is (3C x 120 mm2 CU/XLPE/PVC) ;{4/0} with voltage drop = 2.53 %
C.B rating : 250 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 177 x 2.5 =442 A, lead to 500 A)
3- Glazing Line: I full load= 106 A , so the conductor must have 1.25*106= 132 A
cable length = 175 m then the correct size after applying all factors is (3C x 70 mm2 CU/XLPE/PVC) ;{750 MCM} with voltage drop = 2.7 %
C.B rating : 160 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 106 x 2.5 =265 A, lead to 250 A)
and for main feeder, current carrying capacity =1.25*353+ (353+177+106)=1077 A , cable size 3 (4C X300 mm2 CU/XLPE/PVC) ; { 3 ( 3C x 600 MCM)}
the main C.B = 1500 A is that correct or not ??
Please if the above calculations is correct or not , and if not please advise me
Regards for all
1- Press: 2 Nos. each 250 HP
2- Vertical Dryer: 1 No. , 125 HP
3- Glazing : 1 No. , 75 HP
I did calculations to obtain the conductor & C.B for each motor as follow:
1- Press: I full load = 353 A , so the conductor must have 1.25*353= 441 A
cable length = 155 m then the correct size after applying all factors is 2(3C x 150 mm2 CU/XLPE/PVC) ;{300 MCM} with voltage drop = 2.12 %
C.B rating : 630 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 353 x 2.5 =882 A, lead to 800 A)
2- Vertical dryer: I full load= 177 A , so the conductor must have 1.25*177= 221 A
cable length = 150 m then the correct size after applying all factors is (3C x 120 mm2 CU/XLPE/PVC) ;{4/0} with voltage drop = 2.53 %
C.B rating : 250 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 177 x 2.5 =442 A, lead to 500 A)
3- Glazing Line: I full load= 106 A , so the conductor must have 1.25*106= 132 A
cable length = 175 m then the correct size after applying all factors is (3C x 70 mm2 CU/XLPE/PVC) ;{750 MCM} with voltage drop = 2.7 %
C.B rating : 160 A is that correct or not ?? ( if we follow NEC 430.52, So it must be 106 x 2.5 =265 A, lead to 250 A)
and for main feeder, current carrying capacity =1.25*353+ (353+177+106)=1077 A , cable size 3 (4C X300 mm2 CU/XLPE/PVC) ; { 3 ( 3C x 600 MCM)}
the main C.B = 1500 A is that correct or not ??
Please if the above calculations is correct or not , and if not please advise me
Regards for all