Feeder cable

Status
Not open for further replies.

dog

Member
Does feeder cable for SER cable from a main disconnect need to be protected in a basement to a subpanel in the residential installation(200 amp service)?
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: Feeder cable

There is too little information to answer your question. Are we talking about a residential basement? Has the SER cable been installed in compliance with the rules for NM?
--
Tom
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Feeder cable

Dog, I'm not sure of what you're asking, but if the SER cable is indeed being used as a feeder, it would have to be installed per article 338 which will basicaly instruct you to install it the same as NM or article 334.

Roger
 