I need to deterimine the minimum size of a power source (diesel generator) . The loads are a mixture of things and I know how to get to a normal service size calculated. What is throwing me is I have several good sized motors ranging from 100HP down to 10 HP that are served by VFD and motors not VFD supplied. 430.122 says I take the input current rating at 125% of the nameplate of the drive for conductor sizing. So the questions are:
1) is the drive input current rating used instead of the HP FLA of the VFD supplied motor in 430.250 since this essentially a branch circuit to the drive not to a motor.
2) Does the 125% carry over to the service calculation for each drive or just the input rating?
3) Does the 25% of the largest motor fall to the next largest motor not supplied by a drive or to the largest motor which is served by a drive?
Any help would be appreciated. I am not asking if the real world reduced load seen on the generator is acceptable. I need the hard NEC requirement.