Just want to get some other opinions on a calculation. This is commercial not residential.
I claim that the feeder is too small for the load. It's presently on a 2 pole 30 amp breaker, #10 copper wire that feeds a subpanel.
There's this 'espresso' stand, very small, and I did a calculation that used the 'kitchen equipment' demand factors NEC 2008 220.56. I consider the 'espresso' machine and the 2 coffee grinders kitchen equipment, and someone else does not.
This is a 120/208 feeder 2 hots 1 neutral 1 ground, single phase (of a 3 phase system)
here's my numbers all name plate ratings
espresso machine 208volts (Kitchen equipment) 5200 watts/va
2 coffee grinders (kitchen equipment) 7.5amps at 120volts 900va X 2 = 1800va
refrigerator 4 amps at 120volts 480 va
2 duplex receptacles 180 va each yoke 360 va
Kitchen equipment 90% demand factor 3 units 5200+1800=7000 X .90= 6300va
recptacles 100% 360va
frig 100% 480va
Total 7140
7140/208=34.32amps need a 40 amp feeder #8 wire 2 pole 40amp breaker to feed subpanel 4 wire.
So what do you think?? am I correct in this for considering the espresso and coffee grinders kitchen equipment? What else would you call it??
I claim that the feeder is too small for the load. It's presently on a 2 pole 30 amp breaker, #10 copper wire that feeds a subpanel.
There's this 'espresso' stand, very small, and I did a calculation that used the 'kitchen equipment' demand factors NEC 2008 220.56. I consider the 'espresso' machine and the 2 coffee grinders kitchen equipment, and someone else does not.
This is a 120/208 feeder 2 hots 1 neutral 1 ground, single phase (of a 3 phase system)
here's my numbers all name plate ratings
espresso machine 208volts (Kitchen equipment) 5200 watts/va
2 coffee grinders (kitchen equipment) 7.5amps at 120volts 900va X 2 = 1800va
refrigerator 4 amps at 120volts 480 va
2 duplex receptacles 180 va each yoke 360 va
Kitchen equipment 90% demand factor 3 units 5200+1800=7000 X .90= 6300va
recptacles 100% 360va
frig 100% 480va
Total 7140
7140/208=34.32amps need a 40 amp feeder #8 wire 2 pole 40amp breaker to feed subpanel 4 wire.
So what do you think?? am I correct in this for considering the espresso and coffee grinders kitchen equipment? What else would you call it??