I'm coming up with a feeder calculation for a chiller with the following nameplate info and wanted to make sure I was going about it correctly:
Voltage: 480V
Current consumption max: 7.9A
Current consumption compressor/fan/pump: 5.30A / 2x0.80A / 1.00A
Fuse, max: 15.0A
Starting current LRA: 66A
I'm used to chillers providing a minimum circuit ampacity (MCA) and max protective device size. In this case it looks like they are providing the maximum protective device size but do not provide an minimum circuit ampacity.
Looking at 440.33 it looks like the circuit ampacity is determined by taking 125% of the highest motor-compressor current plus the sum the sum of the other loads. So in this case I see this calculation as follows:
Min circuit ampacity = (5.30 * 1.25) + (2*.80) + 1 = 9.22A which can be covered by a #12 AWG. I'm assuming this would be the same value that the manufacture would list as the MCA on the nameplate if it had been listed and saves the extra step of having to carry out this calculation.
For the maximum protection size it looks like 440.22(B)(1) states that overcurrent device must not be large than 225% of highest motor-compressor load plus the current of the other motors. In this case I see this calculation as follows:
Max overcurrent device = (5.30 * 2.25) + (2*.80) + 1 = 14.5A which is very close to the 15A max fuse size listed on the nameplate.
Am I on the right track here?
For load calculation purposes at the panelbaord feeding several of these compressors would I use the 7.90A value for the load calculation. Are there any adjustment factors that are applied to this value when feeding several of these compressors such as using 25% of largest motor like a motor feeder calculation?
Voltage: 480V
Current consumption max: 7.9A
Current consumption compressor/fan/pump: 5.30A / 2x0.80A / 1.00A
Fuse, max: 15.0A
Starting current LRA: 66A
I'm used to chillers providing a minimum circuit ampacity (MCA) and max protective device size. In this case it looks like they are providing the maximum protective device size but do not provide an minimum circuit ampacity.
Looking at 440.33 it looks like the circuit ampacity is determined by taking 125% of the highest motor-compressor current plus the sum the sum of the other loads. So in this case I see this calculation as follows:
Min circuit ampacity = (5.30 * 1.25) + (2*.80) + 1 = 9.22A which can be covered by a #12 AWG. I'm assuming this would be the same value that the manufacture would list as the MCA on the nameplate if it had been listed and saves the extra step of having to carry out this calculation.
For the maximum protection size it looks like 440.22(B)(1) states that overcurrent device must not be large than 225% of highest motor-compressor load plus the current of the other motors. In this case I see this calculation as follows:
Max overcurrent device = (5.30 * 2.25) + (2*.80) + 1 = 14.5A which is very close to the 15A max fuse size listed on the nameplate.
Am I on the right track here?
For load calculation purposes at the panelbaord feeding several of these compressors would I use the 7.90A value for the load calculation. Are there any adjustment factors that are applied to this value when feeding several of these compressors such as using 25% of largest motor like a motor feeder calculation?