ArtZat
Member
- Location
- Glendale Heights, IL (Chicago Land)
I have a dilemma that I'm hoping you can assist with. I've only done residential and light commercial work thus far but I'd like to grow my business and I have the opportunity to bid on a sizable industrial project. The client has an existing charging station with 20 chargers fed from two load panels. These chargers are 480 volt / 3 phase / 18 amps each. Both load panels are approximately 20 to 30 feet from the chargers.
The client has acquired new chargers to replace the existing ones. However the new charging station will be in a different location in the warehouse. The existing chargers will be removed and the electrical installation supplying them eliminated. My plan is to install one new load panel at the new location for all the chargers. According to my rough distance calculation, the feeder for the new load panel will be approximately 600 feet away from the switch-gear.
Since the chargers will be used for 3 hours or longer and will be used all at once, I'm calculating it as a continuous load. (22.5 amp X 20) which gives me a feeder load of 450 amps. I was thinking of using 2 sets of 350 kcmil in parallel.
My question is whether there is any provision in the code concerning demand factors for fork lift battery chargers. I don't want to price this higher than it needs to be and lose the bid.
I have not been able to find any articles in the NEC specifically pertaining to this installation. Likewise I haven't been able to find any prior posts at this forum.
The client has acquired new chargers to replace the existing ones. However the new charging station will be in a different location in the warehouse. The existing chargers will be removed and the electrical installation supplying them eliminated. My plan is to install one new load panel at the new location for all the chargers. According to my rough distance calculation, the feeder for the new load panel will be approximately 600 feet away from the switch-gear.
Since the chargers will be used for 3 hours or longer and will be used all at once, I'm calculating it as a continuous load. (22.5 amp X 20) which gives me a feeder load of 450 amps. I was thinking of using 2 sets of 350 kcmil in parallel.
My question is whether there is any provision in the code concerning demand factors for fork lift battery chargers. I don't want to price this higher than it needs to be and lose the bid.
I have not been able to find any articles in the NEC specifically pertaining to this installation. Likewise I haven't been able to find any prior posts at this forum.