We are needing to turn a piece of equipment that will require temporary power to some lubrication pumps. This is a new construction project so power is not yet avaliable in the area, so we will need to get power from an existing MCC and run a feeder circuit to a small "portable MCC" arrangement which will have two small starters and two breakers. The following are my loads wich will be fed from the "portable MCC"
All loads are continuous and are rated at 480V:
Motor 1: 24.9A
Motor 2: 24.9A
Heater 1: 1.83A
Heater 2: 1.83A
Adding these 4 loads I come up with 53.46A and taking 125% of the largest motor gives me 66.8A as the connected load off of the portable MCC. Rounding this number up I figure that I will at least need a feeder with an ampacity of 67A to be able to feed this portable MCC. Since the 480V existing MCC being used to feed the portable MCC only has an 100A breaker avaliable I figured that I would have to run a #2 feeder off of the 100A breaker to feed the portable MCC. This would also allow extra capacity on the feeder. Voltage drop will not be an issue.
Does it seem like I have taken the correct steps and made the correct calculations for this application. Do you agree with my design choices?
All loads are continuous and are rated at 480V:
Motor 1: 24.9A
Motor 2: 24.9A
Heater 1: 1.83A
Heater 2: 1.83A
Adding these 4 loads I come up with 53.46A and taking 125% of the largest motor gives me 66.8A as the connected load off of the portable MCC. Rounding this number up I figure that I will at least need a feeder with an ampacity of 67A to be able to feed this portable MCC. Since the 480V existing MCC being used to feed the portable MCC only has an 100A breaker avaliable I figured that I would have to run a #2 feeder off of the 100A breaker to feed the portable MCC. This would also allow extra capacity on the feeder. Voltage drop will not be an issue.
Does it seem like I have taken the correct steps and made the correct calculations for this application. Do you agree with my design choices?