Just saw another job they did with a feeder calculation for kitchen equipment. Very similar to the one I posted about before, here is the calculation
17a 208v = 3536
16a 208v= 3328
(espresso)5200watt
2 900va coffee grinders= 1800va
water heater 2000watts
2 duplex receptacles= 360va
total 15864 va
15864 X .65= 10311.6
10311.6 + 360=10670.6
10670.6/208= 51.4 amps
They used a 50amp breaker/circuit for this run.
Would you sweat the 1.4 amp since technically the circuit is too small for the run?