Angel Electric
Member
- Location
- OBX, NC.
What we have is a Feeder 120/208 four wire in a raceway supplying 10000 VA. nonlinear load continuous load. The raceway containing the feeder will pass through an ambient temp of 25? C. What is the allowable ampacity of this feeder? I get 37 amps and the test booklet I'm working from provides 41amps Referencing 215.2(A) (1)/ 310.15(B) (2) ( A) & (B) (3) (A) / Table 310.15 (B) (16). i need to learn what i'm nto doing correctly or understand that there could be Typo on the test Questions and answers. Please Help? I don't like to move past anything test wise I don't Understand.