Feeder Calculation

Status
Not open for further replies.

jomuta

Member
Location
Brazil
Occupation
student
Good night, I'm doing a main panel calculation, and in this case I have the real electric consumption measurement data for the education building, it is about 184 A, my question is, in this case for the feeders conductors calculation i take the total current of the 184 A and multiply by 1.25 for the selection of the feeder conductor?
 
I don't believe you need the 125% since the continuous loads should have been calculated in the initial calculation
 
Ok, its because in the panel will be added two electric vehicles chargers and a new panel will be necessary, the estimated load for both is 100 kVA and 22 kVA from the ABB, i was thinking only sum the total currents and multiply for 1.25, but i'm not sure if its correct?
 