CAPTMIKE said:
I agree with you and the only issue is actually finding NEC articles to substantiate what I do when applicable.The work has to be done in accordance with NEC and thats where some of the issues are arising,such as applying demands to as much as possible.I again appreciate any and all help .
When I was in the Marines it was strictly "Field Expedient".... No NEC at all..... And if you're in the s'i'ck - the NEC does not apply to you... Contractor?????
A quote from my past:
"OCP is for pussies!"

The only OCP was the generator.... On a few occasions wire lost the battle.
Anyway - since you have been there since 04 - you may have realized that certain military politics and etiquette will dictate who and what is on any load shedding or outage program. You'll want distribution to these at the generator.
Also - one must assume worst case scenario that all AC's are on all the time continuous.... (the areas they serve my never reach temp personnel set them for...) Not to mention rapid growth of load by add-on's down the line... IMO - go big on load, and parallel for the gennies. IMO a number of smaller paralleled sets are best - you can take some out for maintenance when necessary, and bring them back one line when needed. Also easier to link up multiples of similar sized sets. And similarly with the load - you will need to "walk on" the load bit by bit if you ever go completely off. So breaking it up as much as possible right at the gen farm is best. While most sets will handle the in-rush - if it doesn't you have big problems. You'll have to go around shutting things off to get re-started.
What voltage are you going to be distributing? Transformers? Over-head or under ground?
IMO med voltage is out of the question for the environment and safety of personnel. 480Y and transformers sized for, and at each building would be good if you have them available. Calc the load at 100%, and divide that across 4 gen sets of 6 available. And manage the load @ 80% capacity. i.e. when demand is low - take one gen set off line to keep from wet stacking the sets. (Clear dry exaust)
But reading your 2nd to last post and have ordered gen sets already.....
400/230 50Hz - non-US? Or dealing with available shipped equipment? Are the recepticals 230 at 360va? Normal NEC calc'ed values would be 180 per yoke at 120v for GP recepticals.... 230 would be like 60va... Considering the circumstances (which have no equal in the NEC) the AC units would need to be no demand factor applied, as well as lighting - the only fudge area you have is hot water heaters - and from experiance they too should have no demand factor applied - everyone seems to shower at the same time....
Sorry to say there is no way to apply a demand factor to your application. At dusk all the lights will go on, the AC/heater units cranked and everyone is going to shower and shave till the lights go out.