mstrlucky74
- NJ
Here is the scenario:
We need to run a temporary feeders for a tower crane. The total vertical distance 800' but the first run will be to the 5th floor then jumped every 6 floors So essentially a feeder will be run to a box on the 5th floor for the crane then when the crane is moved up a few floors the feeder will have to be spliced and extended up a couple of floors. The load will be 500a fed from a 480v. Engineers/PM calculated thhn Al and it would be two sets of (3)750 +n+g to be run in EMT. I am curious about a few things. Is this the best way to do this?
The calculation of 750mcm is correct(based on VD) but that is based on the 800' run. In the beginning stages the run will be shorter obviously. Can you start will smaller wire then increase the size as run increases? How about running (3) sets of a smaller outdoor rated cable assembly instead of conduit? I say (3) sets because I don't think there is an So or SEU cable assembly that comes in 750mcm. Any thoughts? Thanks a lot