Hi, I'm a new member and I'm a little confused regarding the NEC. Section 215.2 states that the following:
Feeder conductors shall have an ampacity not less than required to supply the load as calculated in Parts III, IV and V of Article 220. The minimum feeder-circuit conductor size before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
The clause seems to be contradicting itself. The methods of article 220 seems to give you a lower number than the %125 x continuous load plus noncontinuous load rule because of the application of the demand factors. And in other websites the methods of article 220 are emphasized. Which is the correct method for sizing a feeder?
Feeder conductors shall have an ampacity not less than required to supply the load as calculated in Parts III, IV and V of Article 220. The minimum feeder-circuit conductor size before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
The clause seems to be contradicting itself. The methods of article 220 seems to give you a lower number than the %125 x continuous load plus noncontinuous load rule because of the application of the demand factors. And in other websites the methods of article 220 are emphasized. Which is the correct method for sizing a feeder?