electro7
Senior Member
- Location
- Northern CA, US
- Occupation
- Electrician, Solar and Electrical Contractor
I have a solar installation that is a bit more complicated.
I have 100A of solar OCPD and I want to tie into a 100A rated sub-panel (B2) in a recreation building. That 100A rated sub-panel is fed from another sub-panel (B1) in the house. It has a 100A feeder breaker with #4 AWG wire. Panel B1 is fed from the main service with #2 and is protected by a 125A rated breaker. The service has a single 240V 400A breaker, single phase.
Here is my proposed design to make this work and my one question I have:
Upgrade the B2 and B1 panel to a 200A for the 120% busbar rule keeping the feeder conductors and feeder breakers the same. Downsize the main breaker to 350A.
My one question is the existing B2 feeder conductors are #4. Am I reading correctly in the 2014 NEC that the feeder conductors can be 83% of the rated ampacity? So in other words #4 AWG is okay with 100A of OCPD?
Is my proposed design within NEC rules on that #4 AWG feeder conductors? There would be 100A of OCPD of solar. 2 inverters, one at 40A the other 60A of OCPD.
Thanks
I have 100A of solar OCPD and I want to tie into a 100A rated sub-panel (B2) in a recreation building. That 100A rated sub-panel is fed from another sub-panel (B1) in the house. It has a 100A feeder breaker with #4 AWG wire. Panel B1 is fed from the main service with #2 and is protected by a 125A rated breaker. The service has a single 240V 400A breaker, single phase.
Here is my proposed design to make this work and my one question I have:
Upgrade the B2 and B1 panel to a 200A for the 120% busbar rule keeping the feeder conductors and feeder breakers the same. Downsize the main breaker to 350A.
My one question is the existing B2 feeder conductors are #4. Am I reading correctly in the 2014 NEC that the feeder conductors can be 83% of the rated ampacity? So in other words #4 AWG is okay with 100A of OCPD?
Is my proposed design within NEC rules on that #4 AWG feeder conductors? There would be 100A of OCPD of solar. 2 inverters, one at 40A the other 60A of OCPD.
Thanks