Want to run this by you and see what you say. An OEM is supplying a piece of equipment. The equipment will consist of (2) 75 HP, 460 V, 3 phase induction motors. These are to be fed by the OEM supplied motor control panel. The OEM panel does not have a main OCPD, but does contain branch OCPD?s for each motor.
I am sizing the OCPD and feeder to this OEM panel. Both motors can be started at the same time and do run at the same time. The OEM panel includes wye-delta starters for the motors.
Step 1: Full load current = 96 amps (NEC 430.250)
Step 2: Standard overload = 96 amps x 1.15 = 110 amp (NEC 430.32(A)(1))
Step 3: Branch circuit conductor: 96 amps x 1.25 = 120 amps => #1 AWG conductor to each motor (NEC 430.22 and 310.16)
Step 4: Branch over current protection: 96 amps x 2.5 = 240 amps => next size up = 250 amp breaker MAX. (NEC 430.52)
Step 5: Feeder conductor: 96 amps (largest motor) x 1.25 + 96 amps (other motor) = 216 amps => 4/0 AWG conductor. (NEC 430.24 and 310.16)
Step 6: Feeder over current protection: 250 amp breaker + 96 amps motor = 346 amps => next size down = 300 amp breaker MAX. (NEC 430.62)
Steps 1 through 4 relate to devices that are inside the OEM panel. Steps 5 & 6 determine the size of the OCPD in my service entrance switchboard and the conductor size from the switchboard to the OEM panel.
My question is?The 4/0 feeder conductor in step 5 is only good for 230 amps. Should this be increased to 300 MCM to account for the 300 amp breaker in the switchboard or is this OK?
I am sizing the OCPD and feeder to this OEM panel. Both motors can be started at the same time and do run at the same time. The OEM panel includes wye-delta starters for the motors.
Step 1: Full load current = 96 amps (NEC 430.250)
Step 2: Standard overload = 96 amps x 1.15 = 110 amp (NEC 430.32(A)(1))
Step 3: Branch circuit conductor: 96 amps x 1.25 = 120 amps => #1 AWG conductor to each motor (NEC 430.22 and 310.16)
Step 4: Branch over current protection: 96 amps x 2.5 = 240 amps => next size up = 250 amp breaker MAX. (NEC 430.52)
Step 5: Feeder conductor: 96 amps (largest motor) x 1.25 + 96 amps (other motor) = 216 amps => 4/0 AWG conductor. (NEC 430.24 and 310.16)
Step 6: Feeder over current protection: 250 amp breaker + 96 amps motor = 346 amps => next size down = 300 amp breaker MAX. (NEC 430.62)
Steps 1 through 4 relate to devices that are inside the OEM panel. Steps 5 & 6 determine the size of the OCPD in my service entrance switchboard and the conductor size from the switchboard to the OEM panel.
My question is?The 4/0 feeder conductor in step 5 is only good for 230 amps. Should this be increased to 300 MCM to account for the 300 amp breaker in the switchboard or is this OK?