aNerdyEngineer
Member
- Location
- Menomonee Falls, WI, USA
I'm struggling with the way to size the protection on a feeder circuit. Our typical system design will have a through-door fused disconnect switch or circuit breaker. The issue I'm finding is the definitions of 'disconnect' vs 'over current protective device'. I would interpret a through-door fused disconnect switch or circuit breaker applicable to BOTH being a disconnect and OCPD. That being said, there are two governing sizes:
1. Disconnect per UL508A:30.2.2.C, NEC:430.128, NEC:430.110, NEC:610.33 (we do cranes & hoists)
2. OCPD per UL508A:32.3.1, NEC:430.62(A), NEC:610.41 (we do cranes & hoists)
If 1) says I need a MINIMUM of 115% sizing for a disconnect and 2) says I have a MAXIMUM size per a combination of the loads, how would a combined device ever meet both of these? What am I missing?
1. Disconnect per UL508A:30.2.2.C, NEC:430.128, NEC:430.110, NEC:610.33 (we do cranes & hoists)
2. OCPD per UL508A:32.3.1, NEC:430.62(A), NEC:610.41 (we do cranes & hoists)
If 1) says I need a MINIMUM of 115% sizing for a disconnect and 2) says I have a MAXIMUM size per a combination of the loads, how would a combined device ever meet both of these? What am I missing?