B bill g Member Nov 21, 2010 #1 if i have a disconnecting means for the feeders to a house on a pole do i still need one on the house
if i have a disconnecting means for the feeders to a house on a pole do i still need one on the house
iwire Moderator Staff member Location Massachusetts Nov 21, 2010 #2 bill g said: if i have a disconnecting means for the feeders to a house on a pole do i still need one on the house Click to expand... Yes, at least very likely, see 225.31
bill g said: if i have a disconnecting means for the feeders to a house on a pole do i still need one on the house Click to expand... Yes, at least very likely, see 225.31
B bill g Member Nov 22, 2010 #3 feeder disconnecting means let me rephrase, if i have a disconnect on the pole and a main breaker on the house do i need an additional disconnect on the house?
feeder disconnecting means let me rephrase, if i have a disconnect on the pole and a main breaker on the house do i need an additional disconnect on the house?
raider1 Senior Member Staff member Location Logan, Utah Nov 22, 2010 #4 bill g said: let me rephrase, if i have a disconnect on the pole and a main breaker on the house do i need an additional disconnect on the house? Click to expand... Provided that the main breaker at the house meets the requirements of 225.32 then you would not need an additional disconnecting means at the house. Chris
bill g said: let me rephrase, if i have a disconnect on the pole and a main breaker on the house do i need an additional disconnect on the house? Click to expand... Provided that the main breaker at the house meets the requirements of 225.32 then you would not need an additional disconnecting means at the house. Chris