The bus maintenance building at a local high school was hit by lightning and burned last July. I am contracted as the electrician on the re-build. The reconstruction is by the original drawings from 1987. The original building was fed with (3) 3/0 THHN conductors in 1-1/2" conduit underground to a 3 phase ML 480V panelboard. The 480V panelboard had a 100A breaker feeding a 45kva transformer stepping it down to 208Y/120 in a 42 circuit panel. The 480V panel also had (5) other circuits feeding (3) Chromalox electric heaters and (2) 2hp OHD operators. When they demo'd out the concrete slab today we discovered the 1-1/2" RMC containing the feeders turned into 1-1/2" sched 40 PVC about 42" below grade. The conduit emerges at the school building as 1-1/2" RMC and continues above the ceiling tile in RMC all the wat to the switch gear in the electrical room. The detatched bus building had a 3/4"x10' ground rod driven outside the building and another 3/4"x10' driven inside the building through the slab. The rods were bonded together with bare #4 and connected to the ground bar in the 480V panel. Is this allowable? I ask because I have to replace the feeder conductors that are fire damaged and assumed the original contractor had gotten by with 1-1/2" conduit for the (3) 3/0 conductors by using 1-1/2" RMC as the EGC. The distance from the bus building to the school building is 160' and 150' of it is a newly paved parking lot. I thought a feeder had to include a grounded conductor or in the case of straight 3 phase an EGC. Am I mistaken? Thanks in advance.