Feeder feeding building disconnect

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Feeder feeding Disconnect A in separate new building A does not fall under exception of NEC 2014 section 250.32(B). Can the disconnect A be regular fused safety switch or does it have to be service rated?
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Look at 225.36.

It says: shall be comprised of a circuit breaker, molded case switch, general-use switch, snap switch, or other approved means. Where applied in accordance with 250.32(B), Exception No. 1, the disconnecting means shall be suitable for use as service equipment.

Does not mention fused safety switch?
 