I am installing a commercial air compressor and drier system. My service is 800A, 4 wire, 240 V high leg delta.
The compressor skid has 2-7 1/2 H P 3 phase belt driven compressors at 22 FLA and 25 FLA (the 25 A motor is 3 wire motor labeled for 200 V) and the drier is labeled 5.6 A, 230 V, 3 phase . I have an unloaded 3 phase 200 A C-H plug-in panel with-in 10 fT of compressor skid. Panel takes type CH breakers. Starters are prewired to motors.
Using one Feeder Breaker per 230.62 (NEC 2014) :
1 st 7 1/2 largest FLA = 50 A
2 nd 7 1/2 FLA = 22A
Drier = 6 A
Feeder Breaker size = 80 A
Am I correct so far? I will protect the drier with 15 A time delay fuses or panel mount 15 A breaker.
My feeder conductor will be:
125 % largest motor = 31.25
second motor = 22
Drier = 6
Total load =59.25 =# 4 AWG xhhw (75 C, CU, XHHW, 100 deg ambient temp)
Agree? If not why.
First time in 50 yrs I have figured 1 feeder breaker for multiple motors. Would normally have MCC bucket for each motor with MCP and starter combination or the Manufacture would have skid disconnects, starters and control pre wired and we would supply feeder breaker and conductor per engineered specks.
Again please confirm or give me directions for corrections.
LRB
The compressor skid has 2-7 1/2 H P 3 phase belt driven compressors at 22 FLA and 25 FLA (the 25 A motor is 3 wire motor labeled for 200 V) and the drier is labeled 5.6 A, 230 V, 3 phase . I have an unloaded 3 phase 200 A C-H plug-in panel with-in 10 fT of compressor skid. Panel takes type CH breakers. Starters are prewired to motors.
Using one Feeder Breaker per 230.62 (NEC 2014) :
1 st 7 1/2 largest FLA = 50 A
2 nd 7 1/2 FLA = 22A
Drier = 6 A
Feeder Breaker size = 80 A
Am I correct so far? I will protect the drier with 15 A time delay fuses or panel mount 15 A breaker.
My feeder conductor will be:
125 % largest motor = 31.25
second motor = 22
Drier = 6
Total load =59.25 =# 4 AWG xhhw (75 C, CU, XHHW, 100 deg ambient temp)
Agree? If not why.
First time in 50 yrs I have figured 1 feeder breaker for multiple motors. Would normally have MCC bucket for each motor with MCP and starter combination or the Manufacture would have skid disconnects, starters and control pre wired and we would supply feeder breaker and conductor per engineered specks.
Again please confirm or give me directions for corrections.