I got a 3/4" EMT and nothing else, and the shop (in high rise) will need only single phase, so with my calcs, i got: 137 mm on the conduit, and 32.7 on each 6 ga, and 23.7 on 8 ga.
I can't quite get 5 conductors 6ga. through, ( like 42%) so would you: set the breakers on the other floor, or pull a single phase 60 amp panel with 4 6ga wires? OR 5 8 ga and build a 50 amp 3phase panel?
I can't quite get 5 conductors 6ga. through, ( like 42%) so would you: set the breakers on the other floor, or pull a single phase 60 amp panel with 4 6ga wires? OR 5 8 ga and build a 50 amp 3phase panel?