Yeah exception #3, my fav. The new set of service conductors would not have to terminate in the meter and could be bugged on to the conductors in that 200 amp disconnect if needed. Only potential disadvantage would be the conductors could only go a short distance in the garage before hitting the service disconnect.Under an exception to 230.40 you can install a set of service conductors to the detached garage directly from the meter socket to the detached garage if your POCO does not object.
Even a feeder supplied separate structure needs the disconnecting means in the building nearest the entry point though.Yeah exception #3, my fav. The new set of service conductors would not have to terminate in the meter and could be bugged on to the conductors in that 200 amp disconnect if needed. Only potential disadvantage would be the conductors could only go a short distance in the garage before hitting the service disconnect.
Oops, yes you are indeed correct about that.Even a feeder supplied separate structure needs the disconnecting means in the building nearest the entry point though.