Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
They're not using the90° C column, they're using the 75° C column and the next size up rule in 240.4(B) as Augie mentioned.@ the 75 degree column two sets only good for 760A. Maybe they are using 90 degree column...................
Would you please give more info when you ask a question. @ sets of what???? at least give the wire size and say whether copper or al. For the number of questions you ask it's the least you could do.@ the 75 degree column two sets only good for 760A. Maybe they are using 90 degree column...................
Excuse you...wire size and sets given.Would you please give more info when you ask a question. @ sets of what???? at least give the wire size and say whether copper or al. For the number of questions you ask it's the least you could do.
I apologize as well. I know I ask a lot of question and must be a PIA. Sorry.My apologies.. I did not click on the pic- I thought that was the entire pic
I think generally most of us don't have a problem with lots of questions, what is frustrating is poor illegible drawings, lack of details, vagueness.I apologize as well. I know I ask a lot of question and must be a PIA. Sorry.
UnderstoodI think generally most of us don't have a problem with lots of questions, what is frustrating is poor illegible drawings, lack of details, vagueness.