@ the 75 degree column two sets only good for 760A. Maybe they are using 90 degree column...................
 

Attachments

  • Capture.PNG
    Capture.PNG
    109.9 KB · Views: 26

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What's your question.
240.4 allows an 800 amp breaker on conductors rated 760 amps as long as the load doesn't exceed 760.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
@ the 75 degree column two sets only good for 760A. Maybe they are using 90 degree column...................
They're not using the90° C column, they're using the 75° C column and the next size up rule in 240.4(B) as Augie mentioned.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
@ the 75 degree column two sets only good for 760A. Maybe they are using 90 degree column...................
Would you please give more info when you ask a question. @ sets of what???? at least give the wire size and say whether copper or al. For the number of questions you ask it's the least you could do.
 

paulengr

Senior Member
Motor breakers are sized 250% of FLA.

Transformers are “oversized”.

The overcurrent protection is based on the load and so is the wiring. The two are not necessarily related. For instance there is the next size up rule and tap rules.
 