I am working on an existing hospital with an attached assisted living facility. There are two electric services involved, one for the hospital and the other for the assisted living.
The hospital has an existing 277/480V/3 generator system with an unswitched grounded conductor. The generator feeds a step-down transformer with 120/208V/3 secondary. A fused disconnect switch is located in the generator room and is fed from the secondary of the transformer. The disconnect serves emergency power to the assisted living facility.
The feeder from the disconnect to the assisted living is (4) #1/0 in a 2" conduit; the conduit is utilized for equipment grounding conductor (EGC). This feeder is approximately 300 feet long and extends to a manual transfer switch in the assisted living. The normal feed for the transfer switch is from the assisted living facility electric service.
The owner is concerned about reliability of the conduit EGC on the emergency feed. My level of concern is much less than the owner's as NEC 250.118 (2005) states EMT, IMC, or RMC are acceptable EGC's. Of course there is a remote possibility the conduit may separate and the grounding connection will be lost.
In an effort to address the owner's concern, I am considering having the contractor install a separate #6 EGC. To avoid pulling the existing feeder out and reinstalling it in the same conduit with the new EGC, I am considering running the new EGC secured with ty-wraps on the exterior of the feeder conduit.
I have looked at the code for guidance with the following results. 215.6 states if a feeder supplies loads which require an equipment grounding conductor the feeder shall include a grounding means in accordance with 250.134.
250.134(B) states that equipment connected by permanent wiring shall be grounded by an EGC contained within the same raceway, cable, or otherwise run with the circuit conductors. This appears to permit the installation of the EGC on the exterior of the conduit unless I have misinterpreted the phrase "otherwise run with".
Have I overlooked pertinent code sections or is my interpretation correct?
The hospital has an existing 277/480V/3 generator system with an unswitched grounded conductor. The generator feeds a step-down transformer with 120/208V/3 secondary. A fused disconnect switch is located in the generator room and is fed from the secondary of the transformer. The disconnect serves emergency power to the assisted living facility.
The feeder from the disconnect to the assisted living is (4) #1/0 in a 2" conduit; the conduit is utilized for equipment grounding conductor (EGC). This feeder is approximately 300 feet long and extends to a manual transfer switch in the assisted living. The normal feed for the transfer switch is from the assisted living facility electric service.
The owner is concerned about reliability of the conduit EGC on the emergency feed. My level of concern is much less than the owner's as NEC 250.118 (2005) states EMT, IMC, or RMC are acceptable EGC's. Of course there is a remote possibility the conduit may separate and the grounding connection will be lost.
In an effort to address the owner's concern, I am considering having the contractor install a separate #6 EGC. To avoid pulling the existing feeder out and reinstalling it in the same conduit with the new EGC, I am considering running the new EGC secured with ty-wraps on the exterior of the feeder conduit.
I have looked at the code for guidance with the following results. 215.6 states if a feeder supplies loads which require an equipment grounding conductor the feeder shall include a grounding means in accordance with 250.134.
250.134(B) states that equipment connected by permanent wiring shall be grounded by an EGC contained within the same raceway, cable, or otherwise run with the circuit conductors. This appears to permit the installation of the EGC on the exterior of the conduit unless I have misinterpreted the phrase "otherwise run with".
Have I overlooked pertinent code sections or is my interpretation correct?