Probably getting a lot of sighs and "not again" with this topic line. I've read many posts over the years concerning Neutral (grounded conductor) as a current carrying conductor for adjustment factor purposes, but have an installation that I would like to run past the forum.
We have a 400A 120/208 3Ø4W feeder to RPP (remote power panel) in data center. This RPP will mainly feed server racks filled with servers with switch mode power supplies that are mainly 1Ø208V (line-line). Because these loads are connected line-line, these loads cannot contribute to the neutral current. For the most part (as much as practical) these loads should be balanced equally A-B, B-C and C-A. There will be some minor loads that are 120V line-neutral for ancillary equipment, but these are very minor loads. I would say maybe 40Amps mostly balanced one each phases A-N, B-N and C-N. This equipment will have switch mode power supplies so I would say that it will have harmonic content. So I have 40A of line-neutral load with harmonic content on a 400A circuit (10%). Should I count the neutral as a current carrying conductor for more that (3) CCC's in a raceway (4 = 80%) per 310.15(B)(3)?
(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral conductor shall therefore be considered a current-carrying conductor.
There will definitely be harmonic content, but most of it will be on line-line so in my option 310.15(B)(5)(c) wouldn't apply here. There will be some line-neutral loads with harmonic content (40A), but this is only 10% of the circuit size and I would not think this would NOT be considered a "major portion" and again 310.15(B)(5)(c) wouldn't apply. I look forward to reading your take on this matter.