Feeder overcurrent protection smaller than panel MCB

Status
Not open for further replies.

cdw238

Member
I am reviewing a set of drawings where a 300-amp main circuit breaker panel is fed from a 250-amp circuit breaker at the swbd upstream of the panel. The designer claims that in this instance the 300-amp main circuit breaker would serve as a disconnect only since the 250-amp circuit breaker would trip in an overload situation. I know this would be acceptable for a main lugs only panel, but it does not seem intuitive for a main circuit breaker panel. The panel is existing, which is why it is a question. Does this sound correct and NEC compliant? I have my doubts.
 
I am reviewing a set of drawings where a 300-amp main circuit breaker panel is fed from a 250-amp circuit breaker at the swbd upstream of the panel. The designer claims that in this instance the 300-amp main circuit breaker would serve as a disconnect only since the 250-amp circuit breaker would trip in an overload situation. I know this would be acceptable for a main lugs only panel, but it does not seem intuitive for a main circuit breaker panel. The panel is existing, which is why it is a question. Does this sound correct and NEC compliant? I have my doubts.

Sounds NEC compliant to me...can't think of any section that it would violate.
 
I am reviewing a set of drawings where a 300-amp main circuit breaker panel is fed from a 250-amp circuit breaker at the swbd upstream of the panel. The designer claims that in this instance the 300-amp main circuit breaker would serve as a disconnect only since the 250-amp circuit breaker would trip in an overload situation. I know this would be acceptable for a main lugs only panel, but it does not seem intuitive for a main circuit breaker panel. The panel is existing, which is why it is a question. Does this sound correct and NEC compliant? I have my doubts.

In general it is not a violation and I see this from time to time for various reasons. The only exception would be if this is an environment where selective coordination is required.
 
The only exception would be if this is an environment where selective coordination is required.


I don't see where coordination would be an issue either...It shouldn't matter which breaker opens first...see, for instance, 700.27 Exception.
 