I have a slightly unusual situation for the service/load center for a single family dwelling.
The main 200A circuit breaker is in an outdoor panel with a load center and auxiliary load lugs.The panel is located 35' from the house on a pedestal.
In the house we have a 200A convertible main lug.The feeder cable from the main disconnect to the main lug is USE 2/0 in a conduit.As the feeder wires ampacity exceed 200A, is it necessary to use an additional and smaller breaker in the main lug? Does NEC 240-21m apply here?
The main 200A circuit breaker is in an outdoor panel with a load center and auxiliary load lugs.The panel is located 35' from the house on a pedestal.
In the house we have a 200A convertible main lug.The feeder cable from the main disconnect to the main lug is USE 2/0 in a conduit.As the feeder wires ampacity exceed 200A, is it necessary to use an additional and smaller breaker in the main lug? Does NEC 240-21m apply here?