WA_Sparky
Electrical Engineer
- Location
- Vancouver, WA, Clark
- Occupation
- Electrical Engineer
Are there any possible issues with the hypothetical situation below regarding not having protection between the utility transformer and the bus feeding two multi family building services. The service disconnects and their respective feeders are sized for their calculated loads. The gear containing the two service disconnects and its feeder are sized for the combined loads of both services. Are we required to provide an additional means of disconnect to protect transformers secondary feeder?
The issue that is coming to mind is in a worst case scenario (even though it should never happen) what if the two services at a later date creep up above 1200A combined, 1300A? Their disconnects may not trip if each individual service is still below their designed limits but the 1200A feeder and bus would burn up. I cant see anything in the code book that says its needed. Is it assumed that the transformer is equipped with a fuse that would protect this feeder?
The issue that is coming to mind is in a worst case scenario (even though it should never happen) what if the two services at a later date creep up above 1200A combined, 1300A? Their disconnects may not trip if each individual service is still below their designed limits but the 1200A feeder and bus would burn up. I cant see anything in the code book that says its needed. Is it assumed that the transformer is equipped with a fuse that would protect this feeder?