Rotaryrocket
Member
- Location
- Monroe, WA
Perhaps someone can help me understand this. I recently did a panel change (strictly panel only, no feeders re-pulled) on a townhome, inspector wrote me up citing 250.32, stating that the EGC must be installed in the raceway.
The townhouse has a PVC conduit run to the service gear. The original feeders pulled through did not have the EGC pulled in the same raceway. The EGC was instead pulled through the building structure to the panel (bare copper #4). If this was good to do back in the early 80's, and I did not alter the feeders, why would this be a violation?
The townhouse has a PVC conduit run to the service gear. The original feeders pulled through did not have the EGC pulled in the same raceway. The EGC was instead pulled through the building structure to the panel (bare copper #4). If this was good to do back in the early 80's, and I did not alter the feeders, why would this be a violation?