Feeder & Service Load Calc in Annex D

Status
Not open for further replies.

Genie

New User
Location
fremont ca
Occupation
electrician
I have some comments and questions about how the 2020 (and previous editions) of the NEC handle the Grounded Conductor Load Calculations

1. In the Example D2(a) and D2(b), the Feeder Neutral Load is adjusted according to table 220.42 and then adds: "In Accordance with 220.61."
I cannot find where in 220.61 it references 220.42. What am I missing? Is it obliquely referring to the unbalanced loads?

2. 220.61 (B)(1) states that before applying 70% demand factor for the feeder neutral, we must use Table 220.55 for ranges and Table 220.54 for Dryers. However, both D.2(a) and D.2 (b) are given as examples of the optional method. I've always been warned away from using tables 220.54 & 220.55 when using the optional method.
Why do the Annex D examples use those tables (in Part III of 220) when using the Part IV optional method. Can someone enlighten me?
 
i am going the calculations on neutral demand in Mike Holts book "Electrical Exam Preparation and I need dome help understanding the neutral demand load calculation. below is a screen shot of the question...i dont understand the neutral demand for the lighting in this example:
 

Attachments

  • Neutral loads.pdf
    995.7 KB · Views: 1