At a wastewater plant I do some work for they want to install 16 - 10hp 460V 3 phase motors for their aeration lagoons. All 16 are to be controlled by VFD's in a separate VFD building close to the lagoons.
My question has to do with sizing the feeder to this building. According to 430.122 (A) these circuit conductors shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment. The rated input of the drives we are using is 15.4 amps. Am I to size the feeder by applying the 125% rating to all 16 drives? 15.4A X 16 X 1.25
Or am I to apply the 125% to ONE drive plus the sum of the other 15; in keeping with 430.22 and 430.24?
My question has to do with sizing the feeder to this building. According to 430.122 (A) these circuit conductors shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment. The rated input of the drives we are using is 15.4 amps. Am I to size the feeder by applying the 125% rating to all 16 drives? 15.4A X 16 X 1.25