Feeder size for Variable Frequency Drives

Status
Not open for further replies.
At a wastewater plant I do some work for they want to install 16 - 10hp 460V 3 phase motors for their aeration lagoons. All 16 are to be controlled by VFD's in a separate VFD building close to the lagoons.

My question has to do with sizing the feeder to this building. According to 430.122 (A) these circuit conductors shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment. The rated input of the drives we are using is 15.4 amps. Am I to size the feeder by applying the 125% rating to all 16 drives? 15.4A X 16 X 1.25

Or am I to apply the 125% to ONE drive plus the sum of the other 15; in keeping with 430.22 and 430.24?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
nichols21vt said:
At a wastewater plant I do some work for they want to install 16 - 10hp 460V 3 phase motors for their aeration lagoons. All 16 are to be controlled by VFD's in a separate VFD building close to the lagoons.

My question has to do with sizing the feeder to this building. According to 430.122 (A) these circuit conductors shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment. The rated input of the drives we are using is 15.4 amps. Am I to size the feeder by applying the 125% rating to all 16 drives? 15.4A X 16 X 1.25

Or am I to apply the 125% to ONE drive plus the sum of the other 15; in keeping with 430.22 and 430.24?

If you are running one feeder for all the VFDs, IMO, the feeder would be sized in the normal way (per 220), and the individual BCs to the VFDs sized at 125%. I do not think the feeder itself has any motor loads at all, thus it should be sized according to 220, and not anything in 430.
 
Last edited:

bob

Senior Member
Location
Alabama
nichols21vt said:
At a wastewater plant I do some work for they want to install 16 - 10hp 460V 3 phase motors for their aeration lagoons. All 16 are to be controlled by VFD's in a separate VFD building close to the lagoons.

My question has to do with sizing the feeder to this building. According to 430.122 (A) these circuit conductors shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment. The rated input of the drives we are using is 15.4 amps. Am I to size the feeder by applying the 125% rating to all 16 drives? 15.4A X 16 X 1.25

Or am I to apply the 125% to ONE drive plus the sum of the other 15; in keeping with 430.22 and 430.24?
How are you making the connection from the VFD to the feeder? Do you have a breaker panel with breakers feeding each VFD?
 
bob said:
How are you making the connection from the VFD to the feeder? Do you have a breaker panel with breakers feeding each VFD?

Yes,
This is a new bldg. In addition to the VFD's there will be an AC unit, some lighting and receptacles.
The plan is for a MDP (with breakers for the drives), a dry type transformer, and a small 120/208 panel.
 