R Randyel1 New User Location Mississippi Gulf Coast Occupation Business Manager Monday at 6:12 PM #1 According to the NEC 2023 code book, can I use copper #4 (4-3WG) to a 125 amp panel if my load doesn't exceed 90 AMPS?
According to the NEC 2023 code book, can I use copper #4 (4-3WG) to a 125 amp panel if my load doesn't exceed 90 AMPS?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Monday at 6:32 PM #2 The load would have to be 85 amps or less and the supply side OCPD would have to 90 amps or less.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Monday at 6:46 PM #3 Randyel1 said: According to the NEC 2023 code book, can I use copper #4 (4-3WG) to a 125 amp panel if my load doesn't exceed 90 AMPS? Click to expand... The panel can be 125 amps but as Don stated you're limited to a feeder OCPD of 90 amps.
Randyel1 said: According to the NEC 2023 code book, can I use copper #4 (4-3WG) to a 125 amp panel if my load doesn't exceed 90 AMPS? Click to expand... The panel can be 125 amps but as Don stated you're limited to a feeder OCPD of 90 amps.