Feeder size required per NEC 2023

According to the NEC 2023 code book, can I use copper #4 (4-3WG) to a 125 amp panel if my load doesn't exceed 90 AMPS?
The panel can be 125 amps but as Don stated you're limited to a feeder OCPD of 90 amps.
 