Feeder size to apart units

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi,
I have a 8-unit apartment unit ,
each 80' - 100' away ,
with 135 A total draw
off the 800A multi-meter service

question is,
Can I feed the apartments (using 310.15 B7) with #1 thhn , cu
through 150A ocpd mounted in meter/main ????

Tanx
 
The answer has not changed since you posted a similar question here:
http://forums.mikeholt.com/showthread.php?t=164316
You can use 310.15(B)(7) (assuming you are in an area using the ''11 Code) for individual dwelling units IF your install meets the criteria spelled out in that section (120/240 volt 3 wire single phase, etc)
 