Nbmarlar78

Member
Location
Jackson, WY
I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.

The size of the sub panel is not really relevant, what is the actual load to be served?

Roger
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
Engineer wants it based on 80% for possible future equipment.

I hope you're thinking of using THHN/THWN assuming when you say PVC; it is going to be below grade.

Bob is right, if an engineer is involved he should have sized it.

You could also run 500KCMIL aluminum, check pricing as it might be cheaper.
 

Knightryder12

Senior Member
Location
Clearwater, FL - USA
Occupation
Sr. Electrical Designer/Project Manager
I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.

According to my VD calculator, 1 set of 350KCMIL AL would limit the VD at 2.36%. 300 AL would be 2.75%. 4/0 CU would be 2.38%
 

Ingenieur

Senior Member
Location
Earth
using 208/3, 160 A and 3%
R from nec table in Ohm/1000'

0.03 x 208 = sqrt3 x 350/1000 x R x 160
R = 0.0643 Ohm/1000'

need selected conductor R to be lower
Cu 300 0.059 (250 is 0.066, close, 3.08%)
Al 500 0.057 (400 is 0.066, 3.08%)

imo go with the 300 Cu or 500 Al since the R values are based on 0.85 pf, which may be low
 