I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.
 
I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.

The size of the sub panel is not really relevant, what is the actual load to be served?

Roger
 
Engineer wants it based on 80% for possible future equipment.

I hope you're thinking of using THHN/THWN assuming when you say PVC; it is going to be below grade.

Bob is right, if an engineer is involved he should have sized it.

You could also run 500KCMIL aluminum, check pricing as it might be cheaper.
 
I am feeding a 200 amp subpanel from an MDP. The subpanel is located approximately 350 feet away. What size THHN wire should I use when considering voltage drop? I have a 4” pvc in place.

According to my VD calculator, 1 set of 350KCMIL AL would limit the VD at 2.36%. 300 AL would be 2.75%. 4/0 CU would be 2.38%
 
using 208/3, 160 A and 3%
R from nec table in Ohm/1000'

0.03 x 208 = sqrt3 x 350/1000 x R x 160
R = 0.0643 Ohm/1000'

need selected conductor R to be lower
Cu 300 0.059 (250 is 0.066, close, 3.08%)
Al 500 0.057 (400 is 0.066, 3.08%)

imo go with the 300 Cu or 500 Al since the R values are based on 0.85 pf, which may be low
 