I have a customer who has put up a two story building to house his wife's sheep shearing/wool/ teaching others/store hobby. The load is small. Receptacles, lights, 2 mini-splits for HVAC. It has been wired with a 200amp service. Not a dwelling unit. He also wants to feed a nearby livestock barn for the sheep. A few lights and receptacles and 8 water trough heaters. I figure never more than max 150 amps for both. Probably much less.
The power co has a transformer approx 760' from the new building. He does not want to give them an easement through his property to set another transformer closer to the new building. He is also insisting he wants 400 amps run to this part of the property. The power co is willing to set a CT cab by existing transformer for us to feed from. His idea is to run 400 amps to the building and then from there another 260' to the barn.
My suggestion is going to be to run 300amps.
Question I have is:
Can I use a 300 amp service rated fused disconnect and parallel 2 sets 4/0 Al to the building? I figure about 3.67% VD with 150 amp load. But would 2 4/0s be compliant for 300 amps?
If he insists on 400 amp, would 3 sets 4/0 al be compliant?
The power co has a transformer approx 760' from the new building. He does not want to give them an easement through his property to set another transformer closer to the new building. He is also insisting he wants 400 amps run to this part of the property. The power co is willing to set a CT cab by existing transformer for us to feed from. His idea is to run 400 amps to the building and then from there another 260' to the barn.
My suggestion is going to be to run 300amps.
Question I have is:
Can I use a 300 amp service rated fused disconnect and parallel 2 sets 4/0 Al to the building? I figure about 3.67% VD with 150 amp load. But would 2 4/0s be compliant for 300 amps?
If he insists on 400 amp, would 3 sets 4/0 al be compliant?