In reality, knowing that this is a new construction, and total loads are not yet known, we have to assume they may at some time in the future utilize the panel to its fullest capacity. Not to what the calculated current loads are. That would be very residential type thinking, but in the commercial/ industrial world where every panel is loaded to its max, we must assume that they will eventually load this 250 amp panel to approximately 200 amps.
I'll guarantee you that knowing this customer, it won't be long before they would use the full 200 amps. This is again why you don't pull 120/208 that far. You pull a 480 volt 400 mp or even 480 200-amp, then install the 208 250-volt for now loads, and have the capability to add another sub panel in the future when they need more power... which they will.
If you're going to spend the money on the labor and conduit and wire... all of which costs the same whether its 250 amps at 208 or 250 amps at 480. the cost for materials and labor are the same. So pull the 480... and have extra power for expansion.
For what they are installing, if they were to land it in the 480 volt switch gear instead of the 208 gear, they'd end up with twice the power capacity with the same costs.
Plus... If all they ever needed at any time now or in the future was only the 250 amps at 208, it still would cost less to pull in a 125-amp 480-volt run in smaller conduit... smaller wire ... easier pull, then put in a transformer at the destination. You just don't drag 208v 800feet through the rafters. That's why the power company doesn't give everybody 120/208, because it's more economical to pull the smaller wires for the 480, and then install the transformer at the destination.