Feeder Size

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Show a 1200A ATS feeding (2) 1200A panels w/ (3) sets #600. Actually thought it might be (3) sets to EACH panel but not sure that could be since it’s only a 1200A ATS.Hope pics came out ok..seemed ok to me.
 

Attachments

  • Capture.jpg
    Capture.jpg
    15.7 KB · Views: 0
  • Capture 2.jpg
    Capture 2.jpg
    12.5 KB · Views: 0

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Can't see any detail in the pic. Sounds like you have a 1200 amp feeder feeding both panels.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
600kcm is rated 420 amps x 3 parallel runs = 1240 amps-- What about de-rating at 70% for 9 current carrying conductor's?

The diagram shows 3 sets in a 4" conduit
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
600kcm is rated 420 amps x 3 parallel runs = 1240 amps-- What about de-rating at 70% for 9 current carrying conductor's?

The diagram shows 3 sets in a 4" conduit

Ah now I can see it. It's 3 sets of 4 conductors each which is separate raceways.
 