Currently I have a #6 480V branch circuit used to feed a welding receptacle. Personel here want a nother receptacle beside this existing one to be able to plug in another piece of equipemnt. The total FLA of both pieces of equipment comes to 79A. The existing #6 circuit is rated for 65A because you have to used the 75deg rating listed in 310.16. I am told that breaker terminals are rated for 75deg so the 75deg rating of wire size must be used.
In this case the 65A is undersized for the combined load of 79A. I was going to put in a new feeder sized correctly for both these loads. Since both the loads are tools they will not be continuous duty and therfore I do not have to take add 125% to combined load.
I am thinking that I can run a #4 good for 85A and protect it with an 80A breaker. Does this sound right?