If I have a 800A 277/480 panel fedding a 277/480 225A panel. What do you base the feeder size off of? The 225A rating? Thanks.
What size load do you anticipate. Do you want 225 amps. If so, then use T. 310.16. Just because the panel is rated 225 does not mean you have to run wire rated 225 amps.
Absolutely -- but you may want to leave a little extra for expansion.How do you calculate the load....I assume based on what that panel(attached) will be feeding.
Absolutely -- but you may want to leave a little extra for expansion.
I apologize. Here is the other schedule and it shows a 3p 200 frame 150 trip to feed the other 225A panel. So I assume it should be sized for 150. What is the frame/trip exactly. The frame is like the housing???? Thanks.
I apologize. Here is the other schedule and it shows a 3p 200 frame 150 trip to feed the other 225A panel. So I assume it should be sized for 150. What is the frame/trip exactly. The frame is like the housing???? Thanks.
Yes you follow what the Engineer of Record put on your plans. You should have a riser diagram depicting the wire and conduit size from your main panel to the sub panel. You are not responsible for the calculation in this case. Don't you have a complete set of "E" drawings?