So I believe the feeder sizes are wrong shown in DIST BD...even the (2) 225A panel UP-1A & 1B should require 4/0 and the 100A panel should be #2's. How do you determine if a neutral is need for these feeds? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    19.9 KB · Views: 0

Ingenieur

Senior Member
Location
Earth
looks like (as far as I can discern)
200 A frame/lug
150 A CB (fuse?)
3/0 good for 200A
looks OK to me (can't verify V drop from the info presented)

as long as my 'guesses' as to what it says are correct lol
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree the panelboard is rated 225 but the breaker is sized at 150 so 3/0 is plenty good....

The neutral is stated on the plan so you must use that size however there is a 100 amp breaker with 3/0 wire and a #8 equipment grounding conductor. I think that #8 is wrong as it must be upsized since the feeder size is larger than needed 250.122(B)
 

JFletcher

Senior Member
Location
Williamsburg, VA
Why do the first two panels have 2" conduit and the last 1 1/4" even tho all 3 are using 3 3/0 ungrounded? Only difference in #3 is a #2 neutral vs 3/0. According to this wire fill chart:

http://www.westernextralite.com/conduit-fill-table

you cannot put more than 1 3/0 in any type of 1 1/4" conduit

How does it read (1) under phase legs? Are these single phase 120V only panels? If so, why does the feeder column read in sets?

Also, shouldnt it read 3 phase 4 wires?
 