I'm working on a hotel space, and effectively one floor of rooms will be fed from a single panel, so I'm trying to size the feeders for that panel. I'm a bit confused though, because 215 and 220 seem to have conflicting instructions for sizing the feeders. I'm working from the 2023 NEC.
Starting with 220. It's important to qualify here that the hotel rooms will not contain kitchenettes, so they do not qualify as dwelling units. Additionally, the mechanical loads are fed from separate panels. So in 220, we head to Part III for Feeder and service load calculations. 220.40 says the calculated load should be not less than the sum of the loads on the branch circuits supplied, per Part II. Part II (220.10) says the branch loads can be calculated based on 220.44 for hotels, which sends us back to Part III. 220.44 says that effectively all the lighting and receptacles in the room can be can be rolled into one VA/Sq Ft calculation using table 220.42(A), so 1.7VA*292 sq ft = 496.4VA.
Let's look at 215 next. 215.2 says the feeders must be sized as not less than the larger of the non-continuous + 125% continuous loads, and the load after any correction factors have been applied in 310.14. So basically a straight load calculation. I can't know the exact loads for the devices, but we estimated:
Mini Fridge & Coffee - 10 Amps
Bathroom - 10 Amps (running a hair dryer)
General Rec and LTG - 6 Amps
If we anticipate these loads per room, it will be 26 A per room, or 26*120=3120VA.
The 215 results are over six times larger than the minimum from 220. They also haven't factored in the diversity - there's no way every room on the floor is using both their coffee machine and hair dryer at the same time. However, I see no exceptions in 215 allowing you to consider diversity in your calculation. And my understanding is that both 215 and 220 apply, so we're stuck with much larger loads. At the panel, if we have 29 rooms, it's the difference between 80A and 252A, which is the difference between a 100A panel and a 400A panel.
Does anyone have any thoughts on this interpretation? Do we need to go with the oversized panels or is there something I'm missing?
Starting with 220. It's important to qualify here that the hotel rooms will not contain kitchenettes, so they do not qualify as dwelling units. Additionally, the mechanical loads are fed from separate panels. So in 220, we head to Part III for Feeder and service load calculations. 220.40 says the calculated load should be not less than the sum of the loads on the branch circuits supplied, per Part II. Part II (220.10) says the branch loads can be calculated based on 220.44 for hotels, which sends us back to Part III. 220.44 says that effectively all the lighting and receptacles in the room can be can be rolled into one VA/Sq Ft calculation using table 220.42(A), so 1.7VA*292 sq ft = 496.4VA.
Let's look at 215 next. 215.2 says the feeders must be sized as not less than the larger of the non-continuous + 125% continuous loads, and the load after any correction factors have been applied in 310.14. So basically a straight load calculation. I can't know the exact loads for the devices, but we estimated:
Mini Fridge & Coffee - 10 Amps
Bathroom - 10 Amps (running a hair dryer)
General Rec and LTG - 6 Amps
If we anticipate these loads per room, it will be 26 A per room, or 26*120=3120VA.
The 215 results are over six times larger than the minimum from 220. They also haven't factored in the diversity - there's no way every room on the floor is using both their coffee machine and hair dryer at the same time. However, I see no exceptions in 215 allowing you to consider diversity in your calculation. And my understanding is that both 215 and 220 apply, so we're stuck with much larger loads. At the panel, if we have 29 rooms, it's the difference between 80A and 252A, which is the difference between a 100A panel and a 400A panel.
Does anyone have any thoughts on this interpretation? Do we need to go with the oversized panels or is there something I'm missing?