I'm reviewing the electrical code to teach other engineers the rules on feeder sizing and want to verify I'm still on the right track. It seems like there's still a lot of confusion among my colleagues with the "80% breaker standard". I'm using NEC 2023.
Example 1:
The below table shows a feeder calculation. Per my understanding of 215.2, the feeder size would be determined by taking the noncontinuous loads plus 125% of the continuous loads. I first determine the noncontinuous load demand factors per article 220 and add those loads to 125% of the continuous load. The final demand value comes out to 284.5A. Other engineers say that breakers are 80% rated and have required that the minimum feeder size be determined by taking an additional 125% of the 284.5A, resulting in a feeder size of 400A (next size up from 355.63). Since I've already applied the 125% to the continuous loads in the calculations, that seems redundant. In this case, I would have the minimum feeder size be the next size up from the demand - 300A. Please note I'm just wanting to determine the minimum feeder size and not taking into account the good design practice of leaving 20%-25% spare capacity for future additions.
Example 2:
Let's say we don't have continuous loads and the feeder only serves non-continuous loads. Per the below table, I would have the minimum feeder size to be 225A (I know this is tight... again, this is only the minimum size and I would typically go bigger in real life to allow for future wiggle-room or owner changes) while other engineers would bring up the 80% breaker rule and say the minimum feeder size would be 300A (222.1x1.25=277.6).
Let me know what you think!
Additional references:
80% Rule Thread (Jraef's post was particularly helpful)
Schneider Article on 80% Rated Breakers
UL 489
Example 1:
The below table shows a feeder calculation. Per my understanding of 215.2, the feeder size would be determined by taking the noncontinuous loads plus 125% of the continuous loads. I first determine the noncontinuous load demand factors per article 220 and add those loads to 125% of the continuous load. The final demand value comes out to 284.5A. Other engineers say that breakers are 80% rated and have required that the minimum feeder size be determined by taking an additional 125% of the 284.5A, resulting in a feeder size of 400A (next size up from 355.63). Since I've already applied the 125% to the continuous loads in the calculations, that seems redundant. In this case, I would have the minimum feeder size be the next size up from the demand - 300A. Please note I'm just wanting to determine the minimum feeder size and not taking into account the good design practice of leaving 20%-25% spare capacity for future additions.
Non-Continuous & Continuous Feeder (Non-Dwelling) | |||
---|---|---|---|
LOAD CLASSIFICATION | CONNECTED LOAD | DEMAND FACTOR | ESTIMATED DEMAND |
R - RECEPTACLE LOAD | 20000 VA | 0.75 (220.47) | 15000 VA |
X - LARGEST MOTOR | 20000 VA | 1.25 | 25000 VA |
MN - MISC NONCONTINUOUS | 50000 VA | 1 | 50000 VA |
MC - MISC CONTINUOUS | 10000 VA | 1.25 | 12500 VA |
TOTAL (VA) | 100000 VA | 102500 VA | |
TOTAL (A @ 208V/3-ph) | 277.6 A | 284.5 A |
Example 2:
Let's say we don't have continuous loads and the feeder only serves non-continuous loads. Per the below table, I would have the minimum feeder size to be 225A (I know this is tight... again, this is only the minimum size and I would typically go bigger in real life to allow for future wiggle-room or owner changes) while other engineers would bring up the 80% breaker rule and say the minimum feeder size would be 300A (222.1x1.25=277.6).
Non-Continuous Feeder (Non-Dwelling) | |||
---|---|---|---|
LOAD CLASSIFICATION | CONNECTED LOAD | DEMAND FACTOR | ESTIMATED DEMAND |
R - RECEPTACLE LOAD | 50000 VA | 0.60 | 30000 VA |
MN - MISC NONCONTINUOUS | 50000 VA | 1 | 50000 VA |
TOTAL (VA) | 100000 VA | 80000 VA | |
TOTAL (A @ 208V/3-ph) | 277.6 A | 222.1 A |
Let me know what you think!
Additional references:
80% Rule Thread (Jraef's post was particularly helpful)
Schneider Article on 80% Rated Breakers
UL 489