jjengineer
Member
- Location
- Houston
- Occupation
- Engineer
Hello - Is there any requirement in the NEC that would include upsizing the hot conductors (not just the neutral conductor) on the secondary feeder, when you go from a standard 277/480V - 120/208V 3-phase, dry-type, delta-wye configuration transformer to K-rated (for instance, K-13 rated) transformer? I've ran across a transformer feeder schedule, for example, that states for 112.5 KVA transformer, use 2 sets of 4#3/0, 1#1/0G, 2" conduit for standard transformer, but 2 sets of 3#4/0, 1#350N, 1#1/0G, 2-1/2" conduit for K-rated transformer. Hot conductor upsized #3/0 --> #4/0, and I've been unable to determine why this is the case.
Thank you for any assistance.
Thank you for any assistance.