FEEDER SIZING LESS THAN 100A

Status
Not open for further replies.

gnu_mike

Member
I thought I had read on this forum that sizing feeders for less than 100A demand utilizes the 60 degree C column from table 310-16.
Is this right?
 
Re: FEEDER SIZING LESS THAN 100A

In reality, I think most terminations are rated for 75 degrees. For example, Square D type NQOD breakers have a note:

10-30 amp breakers are suitable for use with 60 or 75 degree conductors. 35-125 amp breakers are suitable for use with 75 degree conductors.
I assume that means you can use the 75 deg. column if both ends of the wire are landed on NQOD breakers.

STeve
 