S Seekthetruth Member Location Florida Occupation Electrical Apr 19, 2021 #1 400 amp Main breaker disconnect Load side lugs have 250 MCM going to a Main breaker 150 amp Main Breaker panel and # 1 going to a 100 Main Breaker panel. Should the #1 be 1/0?
400 amp Main breaker disconnect Load side lugs have 250 MCM going to a Main breaker 150 amp Main Breaker panel and # 1 going to a 100 Main Breaker panel. Should the #1 be 1/0?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Apr 19, 2021 #2 #1 is 130 amps so you're 3 amps short for the 1/3 minimum. Not sure that I completely understand your setup.
#1 is 130 amps so you're 3 amps short for the 1/3 minimum. Not sure that I completely understand your setup.
S Seekthetruth Member Location Florida Occupation Electrical Apr 19, 2021 #3 infinity said: #1 is 130 amps so you're 3 amps short for the 1/3 minimum. Not sure that I completely understand your setup. Click to expand... Unique setup . Asking for opinions
infinity said: #1 is 130 amps so you're 3 amps short for the 1/3 minimum. Not sure that I completely understand your setup. Click to expand... Unique setup . Asking for opinions