Two questions,
if we follow feeder tap rule, doesn't it all the way have to follow 120 percent or any bus bars three rule when it finally lands to main panel bus bar. Any way final Inverter current will have to go through main panel , Some jurisdiction approves this connection and some doesn't asking again about 120 percent rule.
Two 7600 H SolarEdge inverter output is connected to existing feeder from sub panel. I understand the feeder has to be sized per 240.21(b), but how about using disconnect as a means of tap so you don't have to upsize( 705.12(b(2)(1b)??
SLD attached.
Thank you
if we follow feeder tap rule, doesn't it all the way have to follow 120 percent or any bus bars three rule when it finally lands to main panel bus bar. Any way final Inverter current will have to go through main panel , Some jurisdiction approves this connection and some doesn't asking again about 120 percent rule.
Two 7600 H SolarEdge inverter output is connected to existing feeder from sub panel. I understand the feeder has to be sized per 240.21(b), but how about using disconnect as a means of tap so you don't have to upsize( 705.12(b(2)(1b)??
SLD attached.
Thank you