hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 1200A main service fused disconnect fused at 1200A feeding trough. The trough feeds two fused disconnects one 800A and second 100A with two electric utility meters
The feeder cable size from the service disco to trough is 6 sets of (3#500 kcmil, 1#30G).
The feeder is then tapped to one of the 800A disconnect from trough. The tapped conductor size is 3 sets of (4#500 AL, 1#2/0G)
Questions:
1. Can feeder be copper and tapped conductors be aluminum? NEC 2014 code allows it or not?
2. What size the tapped EHC be 3/0 CU or 250 kcmil AL?
3. Should not the feeder cable number from service disco to trough be 4#500 kcmil not 3#500kcmil? It’s after main service disco but before utility meters